6/28/2018 12:11 PM | |
Joined: 3/3/2016 Last visit: 8/14/2024 Posts: 140 Rating: (0) |
i used holding register 40001....upto length 10. |
Last edited by: siemensuiapl at: 6/28/2018 12:20:50 PM |
|
6/28/2018 12:15 PM | |
Posts: 1283 Rating: (105) |
Did you try to change the MODE to 103 and try whether you can receive any data? Jay
|
6/28/2018 12:25 PM | |
Joined: 3/3/2016 Last visit: 8/14/2024 Posts: 140 Rating: (0) |
I Tried to change Mode 103 given below error will come. 8188 The MB_MODE parameter has an invalid value. |
6/28/2018 12:28 PM | |
Joined: 3/3/2016 Last visit: 8/14/2024 Posts: 140 Rating: (0) |
|
6/28/2018 12:30 PM | |
Joined: 3/3/2016 Last visit: 8/14/2024 Posts: 140 Rating: (0) |
|
6/28/2018 12:30 PM | |
Joined: 3/3/2016 Last visit: 8/14/2024 Posts: 140 Rating: (0) |
|
6/28/2018 12:36 PM | |
Posts: 1283 Rating: (105) |
This photo shows you are reading Input register with address starting in 30001. is it right setting in the PLC?
|
6/28/2018 12:37 PM | |
Posts: 1283 Rating: (105) |
try the address 30001 in the PLC address of MB CLIENT Block. thanks, Jay
|
6/28/2018 12:38 PM | |
Joined: 3/3/2016 Last visit: 8/14/2024 Posts: 140 Rating: (0) |
AFTER CHANGE CONNECTION type 11 Below result. |
6/28/2018 12:39 PM | |
Joined: 3/3/2016 Last visit: 8/14/2024 Posts: 140 Rating: (0) |
|
6/28/2018 12:39 PM | |
Joined: 3/3/2016 Last visit: 8/14/2024 Posts: 140 Rating: (0) |
|
6/28/2018 12:40 PM | |
Joined: 3/3/2016 Last visit: 8/14/2024 Posts: 140 Rating: (0) |
|
6/28/2018 12:41 PM | |
Posts: 1283 Rating: (105) |
MB DATA Address 30001. This is your address. Not 40001. thanks, jay
|
6/28/2018 12:45 PM | |
Joined: 3/3/2016 Last visit: 8/14/2024 Posts: 140 Rating: (0) |
can u send any sample project in Third party device via Modbus TCP. |
6/28/2018 12:48 PM | |
Joined: 3/3/2016 Last visit: 8/14/2024 Posts: 140 Rating: (0) |
in Remote address i have given the Converter Mobbus TCP address.Its ok or not. |
6/28/2018 1:17 PM | |
Joined: 3/3/2016 Last visit: 8/14/2024 Posts: 140 Rating: (0) |
MB_DATA _ADDRESS IS -30001. Find the enclosed shoot |
6/28/2018 1:19 PM | |
Posts: 1283 Rating: (105) |
Please also upload the BUFF DATA? Thanks, Jay
|
6/28/2018 1:23 PM | |
Posts: 3093 Rating: (323)
|
Hello, Regards, |
6/28/2018 1:24 PM | |
Joined: 3/3/2016 Last visit: 8/14/2024 Posts: 140 Rating: (0) |
i have enclosed the Converter setting snap. |
6/28/2018 1:24 PM | |
Joined: 3/3/2016 Last visit: 8/14/2024 Posts: 140 Rating: (0) |
|
6/28/2018 1:28 PM | |
Joined: 3/3/2016 Last visit: 8/14/2024 Posts: 140 Rating: (0) |
|
6/28/2018 1:31 PM | |
Posts: 1283 Rating: (105) |
As Kaul suggested, try to change MB UNIT ID in system blocks of the MB CLIENT to 1 and check whether it is okay. Thanks, Jay
|
6/28/2018 1:39 PM | |
Joined: 3/3/2016 Last visit: 8/14/2024 Posts: 140 Rating: (0) |
i have enclosed the status. |
6/28/2018 1:39 PM | |
Joined: 3/3/2016 Last visit: 8/14/2024 Posts: 140 Rating: (0) |
|
6/28/2018 1:41 PM | |
Posts: 1283 Rating: (105) |
Btw, what is your PLC IP? Thanks, Jay
|
6/28/2018 2:55 PM | |
Joined: 3/3/2016 Last visit: 8/14/2024 Posts: 140 Rating: (0) |
OK ji,i got meter data in PLC . Thanking you. |
6/28/2018 2:55 PM | |
Joined: 3/3/2016 Last visit: 8/14/2024 Posts: 140 Rating: (0) |
|
6/28/2018 2:57 PM | |
Joined: 3/3/2016 Last visit: 8/14/2024 Posts: 140 Rating: (0) |
|
6/28/2018 2:58 PM | |
Joined: 3/3/2016 Last visit: 8/14/2024 Posts: 140 Rating: (0) |
|
6/28/2018 2:59 PM | |
Joined: 3/3/2016 Last visit: 8/14/2024 Posts: 140 Rating: (0) |
|
6/28/2018 2:59 PM | |
Joined: 3/3/2016 Last visit: 8/14/2024 Posts: 140 Rating: (0) |
once again thanks for all. |