i have a problem pls help me. i want to read analog input but i cant becouse the value are 0 and my wiring is ok pls give data about reading and memory area to read.my plc is s7 1200.and my RTD is 3 wire ------------------------------------------------------------------------------------------ |
Last edited by: hajitapala at: 5/4/2016 11:43:59 AMLast edited by: hajitapala at: 5/4/2016 11:45:14 AMLast edited by: Min_Moderator at: 5/4/2016 12:48:35 PMNew subject after splitting |
|
5/11/2016 5:18 PM | |
Joined: 7/7/2010 Last visit: 9/23/2024 Posts: 15217 Rating: (2417)
|
If you open your project in project view, expand the project tree, and then double click on device configuration, now expand your hardware in the middle lower pane until you find the analog input device and channel you have wired the device(s) to. It should show you the addresses you can use to read the values in your PLC programming. Also, if you look to the right of the configuration details in upper middle pane, it shows an overview of assigned I/O memory addresses. Lastly, you must have already downloaded the Hardware configuration matching your needs and hardware setup to the PLC for all this to work the first time.
|