Hello Ms; Interesting project. Your CPU has a PN interface, and it can easily be configured as a PN IO Controller. Your 5 S7-300 CPUs also have a PN interface, they can be setup as IO Devices on the network, and you can easily use the I-Device functionality to send their data into the S7-400, or in WinCC directly. Configuration and Application of the PROFINET I-Device Function https://support.industry.siemens.com/cs/us/en/view/109478798 The Wago PLC (no part number provided, is it a Profinet IO Coupler 750-37x, or a CPU with Profinet interface?) can also be used as part of the Profinet network. You can use gateways without too much problems in your application, especially if you have worked with this equipment before. I personally prefer to avoid them since my experience shows that they add an additional point of failure in the project, but this is up to you. An alternative to the NT 100-RE_EN module could be a Profinet module for the OMRON NJ CPU; this way all the CPUs except the Dalta PLC would be on the same network, exchanging data with the S7-400 CPU: OMRON NJ PLC Profinet: http://www.edata.omron.com.au/eData/NJ/W511-E2-01.pdf The serial interface of the Delta PLC seems to support Modbus RTU; see the following screenshot, taken from this document: Delta Programmable Logic Controller DVP Series www.deltaww.com › DELTA_IA-PLC_DVP_TP_C_EN_20180614_Web Make sure that the gateway you are llooking at supports Modbus RTU, sometimes serial communciation equipment is not enabled for such protocols. Siemens has a serial module for the S7-400 (CP 441-2) and for the S7-300 (CP 341) that can be enabled for Modbus RTU master functions, either through a Siemens package (rather expensive) SIMATIC S7-300/S7-400 Loadable Driver for Point-to-Point CPs: MODBUS protocol, RTU format, S7 is master https://support.industry.siemens.com/cs/us/en/view/1220184 or though an alternative developed by our friend TIBI68 , available for free download on the forum: MODBUS RTU MASTER FOR CP340/341/441-X (NO DONGLE REQUIRED) At first glance your switch design appears correct, but I am not an expert in this field. If you have specific questions I suggest you start a new thread to attract members with specific expertise in this specialty. The PerformanceMoniotor license you show will collect, analyse and generate KPI information from your WinCC 7.4, but you do not explicitely define your selection for WinCC. If you need suggestions on this subject please indicate the licenses you will be using in that part of the project. Hope this helps, Daniel Chartie
|
1/14/2020 11:29 AM | |
Joined: 4/14/2010 Last visit: 8/6/2024 Posts: 525 Rating: (11) |
Thank You! Daniel Chartie, According your Points. 1. Is it Necessary to Change the configuration and download on both side PN IO Controller and as well in IO Devices for I-Device functionality SENDDP"/"RCVDP in SIMATIC Manager V5.6 following example is on TIA is any manual for SIMATIC Manger V5.xx https://support.industry.siemens.com/cs/us/en/view/109478798 2. Yes, It is Fieldbus Coupler 750-370 Wago 3. We have worked with NT 100-RE-RS for Modbus RTU Yes this additional point of configuration and diagnostic also but programming not needed at Slave side except baud rate and ID settings, Can we use CJ1WPNT21 - OMRON PROFINET IO controller for this application, and in this scenario we will require configuration programming at Omron PLC side after inserting the Profinet module in Omron PLC Rack Slot..?? 4. According to Specification Existing Delta PLC DVP28SV11T2 having Dual communication ports RS232 and RS485 MODBUS ASCII/RTU compatible, Is it 6ES7341-1CH02-0AE0 best approach to access the Slave Instead of Gateway.. Should we use OPC 6GK1704-1CW15-0AA0 SOFTNET-IE S7 V15 software for S7, S5-comp. communication..? 5. There is mentioned INTERFACE INCL. CONFIG. PACKAGE ON CD 6ES7341-1CH02-0AE0 Is it require separate Loadable Driver. 6. 6AV6381-2BS07-4AX0 WinCC system software V7.4 SP1, RC 8192 (8192 PowerTags) Licensed software running for Energy Monitoring System. Now we want o add-on 6AV6372-2DG07-4AA0 WinCC/Performance Mon. Basic P, incl. 30 archive variables, for WinCC V7.4 SP1 for monitoring of OEE and KPI, Is it Require Separate license for Process Historian to Save the KPI OR this is included in Package 6AV6372-2DG07-4AA0.? |
MS |
|
Follow us on