7/10/2011 3:53 PM | |
Joined: 10/7/2005 Last visit: 9/22/2024 Posts: 3021 Rating: (1054)
|
Hello Naina I'm not too sure if I understand your question correctly, so here's some general info: You can generally have I/O's in the central rack (the CPU rack) in a Software redundant system. These are however then so called "unilateral I/O's" and only belong to the CPU to which they are connected (in other words, these central I/O's are NOT part of the software redundant systemand can NOT be seen or used by the partner CPU). So while it may be possible to have a Software redundant system with only central I/O's, it would be a pretty pointless excercise (it would be no diffferent than having two seperate CPU's with their own I/O's and a communication link between them). If you require I/O's to be part of the software redundant system (i.e. the I/O's are available forboth CPU's) you MUST use the ET200M DP stations with the redundant IM153's. There's plenty more good info on this subject in the SIMATIC S7-300/S7-400 Software redundancy for SIMATIC S7 manual and I hope this helps. |
Cheers |
|
2/15/2016 7:46 AM | |
Joined: 9/30/2015 Last visit: 9/7/2022 Posts: 23 Rating: (0) |
Dear Frinds : can you give a example program for s7 300 redundancy |