i use plc s7-300 with drive Simoreg 6RA70 connected via Profibus.but in Hardware configuration didn't use drive,is it possible & if possible how? if i have to define in Hardware Configuration say me how & which parameters must set side of drive & side of plc. Splitted from how setting parametr between plc and dc drive. |
Last edited by: O_Moderator at: 8/16/2011 12:42 PMnew subject after splitting |
|
8/17/2011 9:07 AM | |
Posts: 49 Rating: (0) |
on drive show me fault 82,who can help me? |
8/17/2011 9:26 AM | |
Joined: 3/21/2006 Last visit: 9/10/2024 Posts: 10228 Rating: (1181) |
Hello, F082 means Profibus fault. So seems your drive is already set it to exchange data via Profibus. Yes, you need to assign the drive in hardware configuration. There is needing a GSD corresponding to the type of CB used. (http://support.automation.siemens.com/WW/view/en/48172137). After depending of the numbers of exchanged words (which should be configured in 6RA70 also) select and add them in harware configuration. Take a look at Connection of Masterdrives to Profibus-DP. The logic is the same . Best regards, Hristo Mihalev |