4/22/2013 1:13 AM | |||
Joined: 9/27/2006 Last visit: 9/19/2024 Posts: 12282 Rating: (2684) |
Hello Anil; I do not know of any sample code specifically for a 1SI Modbus RTU master woith a Sitrans FUS 1010. However, if you understand Modbus RTU, even basically, then you should be able to setup the Modbus exchanges rather easily with the following information: First, documentation on the 1SI Modbus master:
You will find links to the 1SI manual and sample programs, and a bunch of FAQs in the Entries tab. Then, this file shows an example of Sitrans FUS 1010 using Modbus with master Modscan32; you can use the register addresses of the values shown as part of the Modbus mapping of the Sitrans to setup your own Modbus exchanges with the 1SI. If your knowledge of Modbus RTU is skimpy or needs refreshment, open the following presentation prepared by our friend smiffy, it really is a very complete and understandable starting point: |
||
Last edited by: dchartier at: 4/22/2013 1:14 AM |
|||
5/26/2017 12:40 AM | |
Posts: 1 Rating: (0) |
The sitrans f 1010 device restarts every 5 minutes |
5/26/2017 12:24 PM | |
Joined: 9/27/2006 Last visit: 9/19/2024 Posts: 12282 Rating: (2684) |
Hello Jorge; There is a Troubleshooting section in this manual for the Sitrans FUS1010 clamp-on flownmeter, see if your unit's behavior is analysed there: Sitrans FUS1010 Operating Instructions If you find no help in the manual, you should try to contact Siemens Support (through the Support Request link at the top of this page) and explain your problem in detail (with all part numbers of hardware and software in your project). They may be able to diagnose if your unit is in need of repair at a Siemens facility. Hope this helps, Daniel Chartier |