9/27/2017 11:26 AM | |
Posts: 27 Rating: (0) |
On the other hand, if we say S7-400 with fault tolerant, does it mean that this is a redundant CPU system? Thank you. |
9/27/2017 2:32 PM | |
Joined: 9/27/2006 Last visit: 4/16/2024 Posts: 12256 Rating: (2663) |
Hello lalabmi; S7-400H Fault-Tolerant systems are designed as redundant configurations. You can examoine the specifications here: S7-400H SIMATIC Fault-tolerant systems S7-400H Siemens proposes libraries for Modbus TCP for S7-400 and S7-300 CPUs under the name "Open Modbus TCP". There are redundant variations of Open Modbus TCP for S7-400H systems, and you have to select between different licenses, for a pair of CP 443-1 or the integrated PN port of the CPUs. More information here: Read more on versions of the redundant Open Modbus TCP licenses: What are the differences between Simati Modbus/TCP Redundant V1, V2 and CP Redundant? Hope this helps, Daniel Chartier |
Last edited by: dchartier at: 9/27/2017 2:35:40 PM |
|
9/28/2017 10:26 AM | |
Posts: 3093 Rating: (322)
|
Hello Lalobmi, Block library for redundant Modbus/TCP communication via CP443-1 or CP343-1 Regards, |