Joined: 10/10/2005 Last visit: 8/29/2024 Posts: 1917 Rating: (136) |
Hello Vijayan.R In order to keep a data block, marker, timer or counter remanent in an IM151 CPU, you must define the memory areas in the CPU properties in the hardware configuration. See the informations of the FAQ: How can you keep data blocks, markers, timers and counters remanent in an IM151 CPU in the case of a power failure? Cicero |
7/23/2019 6:24 PM | |
Joined: 9/27/2006 Last visit: 9/21/2024 Posts: 12282 Rating: (2684)
|
Hello vijayan; In a S7-400 CPU, all DBs are retentive, if program memory is backed-up by battery power: Retentivity behavior of S7-400 CPUs and the CPU 318-2 CPUs https://support.industry.siemens.com/cs/ww/en/view/23596519 However, and that is often irritating, the data that is retained in a DB are the Declaration values (those that are entered at the creation of the DB), not the Actual values (those that are input during programming execution). So in case of a Power Off or Warm Restart, you may find your self with the original setpoints in your DBs, not the present values you are expecting. Here is a procedure that you can implement easily to transfer Actual values to the Declaration view so that they become the values that are retained in a DB: How can you back up the actual values of DBs and markers? https://support.industry.siemens.com/cs/us/en/view/18778977 Hope this helps, Daniel Chartier |
Last edited by: dchartier at: 07/23/2019 18:25:29 |
|