1/7/2017 7:23 PM | |
Posts: 10 Rating: (0) |
Hi all, Can you tell me what is the problem and solution if the diagnostic buffer event is alignment error when writing/reading? |
1/7/2017 7:39 PM | |
Joined: 1/21/2013 Last visit: 9/4/2024 Posts: 4620 Rating: (707) |
Hello, https://support.industry.siemens.com/tf/ww/en/post/613134/ perhaps if you share to us your diagnostic buffer may help you |
1/8/2017 8:23 AM | |
Posts: 10 Rating: (0) |
This is the error |
1/8/2017 8:52 AM | |
Posts: 10 Rating: (0) |
Hi, How do I search? |
Last edited by: fedfp03 at: 1/9/2017 7:20:02 AM |
|
1/8/2017 9:21 AM | |
Posts: 10 Rating: (0) |
It is not called in any OB |
1/8/2017 9:30 AM | |
Joined: 12/9/2010 Last visit: 10/8/2022 Posts: 623 Rating: (77) |
Hi fedfp03, This is error due to indirect addressing. 1. You have to test FC individually with some arbitrary input paranmeters. Ascertain valid limits of input parameters. 2. If it's ok, then check how various inputs are transferred and they are within limits. |
If you like the comment, rate it (right top) or thank it (left bottom). |
|
1/10/2017 4:46 AM | |
Posts: 10 Rating: (0) |
Thank you all for your response. We replace the CPU and now its ok. |