8/30/2017 7:25 PM | |
Joined: 9/27/2006 Last visit: 9/23/2024 Posts: 12282 Rating: (2685)
|
Hello Jabbi; You are showing us the amount of local data available to your FCs and FBs, in your existing CU. You cannot use that information to add to the number of FCs you can use. In your earlier thread it was determined that you have used up all your available ressources for FCs. You do not have very many options: - change to a newer CPU , with up to 5000 FCs; you could look at the technical data for the successor model for your CPU: 6ES7416-3XS07-0AB0CPU 416-3, 16 MB working memory 3 INTERFACES Validate if your version of step 7 supports this new model of CPU. https://support.industry.siemens.com/cs/pd/693841?pdti=pi&lc=en-FR - eliminate unnecessary FCs in your existing program, either by determining those that are not useful in your project any more (use the system ressources menu to see which ones), either by reprogramming them in available FBs (with Instance DBs), either by integrating the code for some FCs inside already existing ones and freeing those up. If you use this option, consider the amount of available memory in load and work memory. once your changes are done make sure to compress you available memory. Hope this helps, Daniel Chartier |
Last edited by: dchartier at: 8/30/2017 7:28:15 PM |
|
This contribution was helpful to2 thankful Users |