Helloacadena, I'm sorry. You can't use the CP443-1 as a Profinet IO controller. The current version of H-CPUs (V6.0.X) supportsonly one integrated IO controller and zero IO controller via CP. I also believe that 200 stations are a bit heavy even for 417H. It has a big memory but think about the communication load for whatever operator interface (Server/PC/HMI ) you will have. Maybe 2 or 3 smaller controllers will do the job better. Best regards, H-H
|
This contribution was helpful to1 thankful Users |
4/27/2014 2:32 PM | |
Joined: 7/2/2008 Last visit: 8/26/2024 Posts: 928 Rating: (308) |
Helloacadena, I'm afraid you won't be able to connect your SINAMICS S to the 2 CPUs of the H-System. Please, check thisthread. If I were you, I would have asked myself/my customer "Do you really need a fault tolerant CPUs in 'roll table' application?!". I recommend a single 400 CPU either with an integrated Profinet IO controller or with multiple CP443-1 as Profinet IO controllers. Best regards, H-H
|