5/23/2014 2:36 PM | |
Joined: 11/21/2007 Last visit: 8/12/2024 Posts: 2325 Rating: (308) |
Hello AK123 First of all you should not normally have CPU memory >80% full . Having said that : a) Optimise your PLC Program to reduce size. b) Minimise the Redundant Data Area ( No and size of Data blocks& Flags ) c) Ensure that all the Redundant DBs are in continuation ( No missing blocks ) d) Use a Profibus CP342-5 for Redundancy connection ( You can go upto 12MBPS instead of 187.5kbps of MPI ) e) Use a Higher CPU Hope this helps Cheers Navnag |
There is no such thing as the last bug in a program |
|
5/30/2014 7:06 AM | |
Posts: 19 Rating: (0) |
Hello, Are you using a individual network channel as SCADA stand-by link? |
Last edited by: rg-link at: 5/30/2014 7:15 AM |
|
6/2/2014 4:17 PM | |
Joined: 9/7/2007 Last visit: 8/30/2023 Posts: 550 Rating: (61) |
HiPrads To test your software and switching time. first connect ONE WinCC Station to the redundant PLC and try a test appliccation for the WinCC and CPU software, also read this manual "SIMATIC S7-300/S7-400 Software redundancy for SIMATIC S7" well and revise all setting on the PLC and WinCC. If you got a reasonable change-over switching time, then try the next step to add a WinCC redundant station and make all possible switching tests, until you get satisfied to the results. Finally, add the clients and operate the application software that you have. |
Best Regards |
|
6/3/2014 6:43 AM | |
Posts: 34 Rating: (0) |
Thanx for your suggestion...I'll try this. |
6/5/2014 6:43 AM | |
Posts: 34 Rating: (0) |
For my above mentioned problem is it necessary to make open ring type protocol in managed type ethernet switch...? |