If I change P701 from 200% to 100% . doesn't it affect to the output current ? |
4/15/2016 10:16 AM | |
Joined: 4/23/2010 Last visit: 12/31/2023 Posts: 8092 Rating: (877) |
Hello, P701 has nothing to do with current. P701 is to normalise analog set point at terminal 4 & 5. After setting it 100 %, check r001 where you will find the set point fed at 4 & 5 terminal i.e. if 1 volt is applied at 4 & 5 terminal, r001 should display 10 (It displays % of set point.) In your case set point signal type is 0-10V refer P700 = 0, so 1volt set point correspondence to 10%.
Please refer the attached sheet of function diagram of analog set point for more information. Motor current depends upon load. HTH. Attachment6RA70 analog set point .pdf (292 Downloads) |
Last edited by: PISCEAN 2010 at: 4/15/2016 10:22:43 AM |
|
4/15/2016 12:16 PM | |
Posts: 64 Rating: (0) |
OK Thank you . I think r001=124 in maximum . so how much do I set P701 ? |