Hi Eli, if I understand right, you want the panel to be a gateway between the build-in PLC's of your Sijects. This is not possible, respectively, for a few tags only. I would prefer a communication between the PLC's, in which the OP177B is connected to all PLC's. This FAQ might help you: http://support.automation.siemens.com/WW/view/en/25735422 Note: The quantity of connections of each PLC is limited, as well as for the OP177B. The OP177B supports only 4 connections. |