7/21/2013 11:00 AM | |
Joined: 4/23/2010 Last visit: 12/31/2023 Posts: 8092 Rating: (872) |
Hello, NC,PLC data needs to be reloaded. Please follow this link for more information. |
Last edited by: PISCEAN 2010 at: 7/21/2013 12:09 PMLink added |
|
7/22/2013 8:33 AM | |
Posts: 166 Rating: (1) |
Sir Thanks for ur reply 1. As per procedure, v kept S3 in 1 and switched ON, then v got 6, +5V Green and SF Red got ON, put back S3 to 0 2. On the other side, PR(green), PS(Red),PF(Red) and PFO(Orange) - all 4 keep blinking, due to this v r unable to follow steps for PLC General Reset 3. As informed before, there was no 24V supply to MCP, hence connected 24V seperately, all LEDs on MCP keep blinking due to communication failure between MCP and CCU Kindly advice Best Regards, M. Rishikesh |
7/22/2013 9:00 AM | |
Joined: 4/23/2010 Last visit: 12/31/2023 Posts: 8092 Rating: (872) |
Please find attached here with the proceduer of clearing NC/PLC data & reload it again. Please follow the sequence. Please select the back up data which was taken while machine was in healthly condition.
Attachment810D NC PLC clear & reload proceduer.pdf (448 Downloads) |
7/22/2013 10:53 AM | |
Posts: 166 Rating: (1) |
Sir V successfully followed such procedures in our other 840D machines but as LEDs keep blinking, unable to do PLC reset |
7/22/2013 11:16 AM | |
Joined: 4/23/2010 Last visit: 12/31/2023 Posts: 8092 Rating: (872) |
Hello, Can you go on line & check if you can establish the communication with Step 7? |
7/22/2013 12:56 PM | |
Posts: 166 Rating: (1) |
Sir Under "Upload to PG", I am able to get accessible nodes under MPI address =1,14 but field under CPU Type is blank so can not upload to PG SF LED is ON in S7300 CPU Regards, M. Rishikesh |
7/22/2013 1:36 PM | |
Joined: 4/23/2010 Last visit: 12/31/2023 Posts: 8092 Rating: (872) |
Hello, One doubt. Data back up which you are trying to restore is of which type? Is it series start up or arc files? Please check. |
7/22/2013 1:49 PM | |
Posts: 166 Rating: (1) |
Sir V r not trying for backup because screen just shows Siemens 810D and does not move ahead to show us Normal Position screen etc, if v press say Machine key etc, we get message waiting for connection... No communication partner etc Kindly advice on how to reset PLC Important observations r that all 4 LEDs on right side ie PR,PS,PF,PFO blinking, SF LED is ON in S7300 CPU plus all LEDs on MCP ( Machine control Panel) blinking Regards, M. Rishikesh |
7/22/2013 2:07 PM | |
Joined: 4/23/2010 Last visit: 12/31/2023 Posts: 8092 Rating: (872) |
Please check the attached sheet. It may help you.
Attachment810D overall reset.pdf (328 Downloads) |
7/22/2013 4:01 PM | |
Posts: 166 Rating: (1) |
Sir Now we put S3 to 1 and S4 to 3, pressed Reset then on the right side PS is blinking and PF is Red Changed S4 to 2 then to 3 to 0 to 2 pressed Reset, Now Only PR is Green Finally put back S3 and S4 to 0 and Now finally on left side, Green for +5V, Red for SF are continiously ON, CB (Orange) blinks On the right side, PR is Green Now v r able to get Position screen etc Error 120008 : Operator Units Switchover PLC Time out 1010 Kindly adviceif above status of LEDs is ok and reasonfor Error 120008 v r not able to get connected with PG using MPI shall v try reloading NC and PLC backup using RS232 ???? Regards, M. Rishikesh |
7/22/2013 4:32 PM | |
Posts: 2964 Rating: (478)
|
Hello, 120008 Control unit switchover, PLC timeout: %1 Parameters: %1 = -- Definitions: 001: MMC would like to go offline from this NCU. MMC has made the offline request in the online PLCand is waiting for the positive / negative acknowledgement from the PLC. 002: MMC would like to go online to this NCU. MMC has called the target PLC and is waiting for the release to go online. 003: MMC has requested the active operating mode and is waiting for acknowledgement from the PLC. Remedy: Check whether the switchover blocks are loaded and started in the online PLC Ensure you have cleared your NC and PLC properly....try doing it again If you have Simatic Step7 software you can clear your plc from this and check too.... goto Plc> diagnosis > Clear and Reset select this your PLC is going to be cleared Check it out and revert back... Regards, Prakash |
7/23/2013 9:21 AM | |
Posts: 166 Rating: (1) |
Sir Thanks for continious support a) We feel that as all LEDs on MCP keep blinking, may be due to that PLC was not going ONLINE hence we taken out cable from PCU on MPI port of CCU and connected MPI directly then it went ONLINE then did upload to PG. Opened blocks then PLC - Diagnossi/Settings- Clear/Reset, PLC Goes to STOP state to clear then we go to operating modes, do warm restart then PLC comes to RUN mode When v did upload to PG, blocks contained only System Data, FB15 and DB1 - can v say that PLC got completely reset with this ????? Pl confirm b) At the moment, S7300 CPU has no SF (System Fault) rather just green LED for +5V is ON, on CCU, left hand side, Green LED for +5V, SF (Sinumerik Ready) RED and CB (orange) is blinking, on right side only Green LED for PR (PLC Run) is ON - Please confirm if CCU is healthy and NC,PLC got erased or not with this indication c) we still keep getting error 120008 Operator Units Switchover PLC Timeout 1010 - sir is it due to faulty MCP ????? Kindly advice Regards, M. Rishikesh |
7/23/2013 10:27 AM | |
Joined: 4/23/2010 Last visit: 12/31/2023 Posts: 8092 Rating: (872) |
Hello, From the so far post, I summaries the points as below. 1. It seems that NC, PLC data is not geting clear correctly. 2. As suggested by Mr. Prakash (Ekalavya), have you checked the cards holding tightness,loose connection of data cables etc. 3. By chance at any time, have you or any other person has unpluged/pluged PCMCIA card on module? I would like to suggest you to contact Siemens service department. |
7/23/2013 2:00 PM | |
Posts: 166 Rating: (1) |
Dear Sirs (M/s PISCEAN 2010, Prakash) We could fix the problem by reading in old NC and PLC archieve (Service - Data In - NC Card - Start), although there is no card plugged on to CCU, may be from EPROM of CCU, v could get these archieve Now MCP is communicating and we could switch ON the control, Hydraulics etc Actually SF Red LED was confusing us as it was ON and it is still ON, in another 810D controller, this SF is OFF Then we also got error 2001 : PLC has not started up Thanks to you all sirs for such a tremendous and continious technical support Best Regards, M. Rishikesh |
This contribution was helpful to1 thankful Users |
7/24/2013 5:57 AM | |
Posts: 2964 Rating: (478)
|
Hello, Your welcome for comments... But i still suggest you can go to Simatic Manager open it and connect it.....go to Diagnostic /setting > Module information > Diagnostic buffer you can see why the PLC has gone to Stop mode...Check here.. Regards, Prakash |