3/25/2016 9:35 PM | |
Joined: 12/27/2006 Last visit: 8/18/2024 Posts: 1197 Rating: (113) |
Online simulation is not possible with LOGOSoft. You can look at the running programming in the LOGO when your programm on the computer is exactly the programm on the Logo. Notice that online look at the working programm is verry slow, so you have an encoder you must turn it very slow. iF you turn to fast you cant see the right working of the input, but the value of the connected Block become right on your PC screen, but a little late. Also in simulationmode on your PC screen (with no LOGO connected) is not verry quick. De real LOGO is much faster than simulation. Oh.. I read ...... Open Collectir output means that you cant directy it to the LOGO. The logo must havenon + Input, so you must use an open emmitir output of your ecoder, You can also use an Pull-Up resitor (about 1 kOhm) between the + and te Digital input. So your encoder can "sink" the signals. Try it! |
Last edited by: Toeternietoe at: 3/25/2016 9:44:22 PM |
|
3/25/2016 9:44 PM | |
Joined: 12/18/2014 Last visit: 9/25/2024 Posts: 33837 Rating: (4205) |
If the supply voltage for the encoder is not the same as for the Logo, you need the M (0V) connect of both voltages together or as a supply voltage for the encoder is the same as for the Logo. |
3/25/2016 11:00 PM | |
Joined: 10/8/2015 Last visit: 9/5/2024 Posts: 62 Rating: (3) |
Of course the power supply is the same, otherwise the encoder will not work properly with the LOGO!. I put a 10 kohm pull-up resistor, and it worked perfectly!!!!! THANK YOU !!!!!! |
This contribution was helpful to1 thankful Users |
3/26/2016 5:49 AM | |
Joined: 12/18/2014 Last visit: 9/25/2024 Posts: 33837 Rating: (4205) |
What did you mean because then with this sentence? |
3/26/2016 5:59 PM | |
Posts: 5225 Rating: (1192) |
Hi Pyrus. You make no mention of which LOGO you downloaded to for the online test. You must use a transistor type (24V) LOGO and not the relay type. Do know the special input must be connected directly to the count pin of the counter. Only then will the 5khz be possible. The input on-off thresholds on the LOGO is different than that of the S7-1200. Check with a voltmeter what the voltages are that you get from the encoder. A 10kohm pull-up resistor sounds high. 1.2kohm (0.5W) resistor is closer to what I expect. I assume you are using only one phase........ which are you using? Again test with the voltmeter to see if the voltages change (if it is not the one you know is working). Maybe share also the program segment you are testing and a sketch of the electrical connections... just as a double check |
3/26/2016 6:07 PM | |
Joined: 12/18/2014 Last visit: 9/25/2024 Posts: 33837 Rating: (4205) |
Why this?
|
3/26/2016 6:15 PM | |
Posts: 5225 Rating: (1192) |
I am so glad you mention this. (information extracted from Appendix A of LOGO! Manual, 06/2014, A5E33039675) ..while.. Your thoughts? |
Last edited by: William_B at: 3/26/2016 6:18:06 PMadd document information |
|
3/26/2016 6:29 PM | |
Joined: 12/18/2014 Last visit: 9/25/2024 Posts: 33837 Rating: (4205) |
The 24V Logos (0BA8) are available as: These logos the data of the digital inputs are identical, 4 Hz for normal input and 5 kHz for fast counting input. Then there is this: This does not fast count inputs, because you can also be operated with 24VAC. |
Last edited by: ixo65 at: 3/26/2016 6:32:10 PMLast edited by: ixo65 at: 3/26/2016 6:42:27 PM |
|
This contribution was helpful to1 thankful Users |
3/26/2016 6:42 PM | |
Posts: 5225 Rating: (1192) |
aaah yes now I remember.... The specifications on that.... Our factory bought the "24RCE" type which was wrong for the application. |
Follow us on