1/10/2018 4:42 AM | |
Joined: 4/23/2010 Last visit: 12/31/2023 Posts: 8092 Rating: (877) |
Hello, Please download 6RA22 drive manual, refer chapter 5 Start up. Follow the steps as explained to enter motor related parameters in respective fields, ( no optimisation is possible).Connect toggle switches to apply CR & drive start commands at X1:18 & X1:17 respectively. Connect X1:23 to X1:24 so that +10 V refernce voltage will be applied. Set P76 = 1 i.e. external field applied since in your case no motor is connected. Refer circuit diagram on page 31 to 33, depends upon your supply voltage levels & drive specification. Connect power to contactor, two phase at X2:2U & 2W terminal, connect two lamps atleast 100W rating inseries across DC output terminals, 1C 1D. Apply control enable & drive commands, you should get maximum DC voltage at DC output terminals & lamps should glow. HTH. |
This contribution was helpful to1 thankful Users |
1/24/2018 4:49 AM | |
Joined: 4/23/2010 Last visit: 12/31/2023 Posts: 8092 Rating: (877) |
Hello sinumerkreza, From your circuit, 230 Volt supply is directly connected to drive, which should not be. You need to apply this power thru contactor which is controlled from K2 relay of A2 card. Power should be applied to drive only after enabling X:17 & X:18 comand i.e. drive start. & CR. Please refer the modified circuit in attachment. Set the field current first & check as per procedure explained in Start up. Best of luck. |
Follow us on