9/9/2014 4:38 AM | |
Posts: 20 Rating: (0) |
Dear All, I have a problem with SIMOREG DC Master 6RA70, the operating status display indicated o10.3, which is on the manual shown that "E-Stop (safety shutdown) has been input via terminal 105 or or 107". So, I tried to check the input and the wiring diagram, please check my attachment. By the way, my conclusion is there was a damage on the internal power supply of Simoreg DCM for 24vdc, do you have any ideas where I can check the circuit diagram? I can't find it on the manual which one is the power supply unit. I also checked the fuses and it's OK. Is there any other fuse where I can check on the internal circuit of Simoreg DCM? best regards, Arsy
AttachmentSimoreg DCM Fragen1.pdf (296 Downloads) |
9/9/2014 5:16 AM | |
Joined: 8/25/2006 Last visit: 9/20/2024 Posts: 2209 Rating: (278) |
Yes, you are right, there should be 24VDC at terminal 106. |
This contribution was helpful to1 thankful Users |