10/18/2010 11:31 PM | |
Joined: 7/28/2010 Last visit: 8/31/2024 Posts: 184 Rating: (11) |
JJ, Take a look at the attached file. Recommended Motor Module for your unit is 6SL312x-xTE21-8AAx which is a9.7KW,18A motor module. Regards, Behnam CPU315 <-> S120, How????? AttachmentSynchronous Motor 1FT7.pdf (365 Downloads) |
10/19/2010 12:29 PM | |
Joined: 7/28/2010 Last visit: 8/31/2024 Posts: 184 Rating: (11) |
JJ, Based on the manual, you have to change the motor module and go for 9.7KW. You can ask customer why they have selected the existing module. You can even skip the auto tuning for now and start running the drive but you may not be able to reach the torque you may require in future. Regards, Behnam www.sigmaprocess.ca/blog |
10/19/2010 2:02 PM | |
Posts: 12 Rating: (0) |
Good and Thank you for your advice |
10/26/2017 9:25 AM | |
Joined: 5/12/2006 Last visit: 9/20/2024 Posts: 22365 Rating: (3011)
|
which motor and which motormodule you use? |
10/26/2017 1:12 PM | |
Joined: 5/1/2015 Last visit: 9/20/2024 Posts: 102 Rating: (0) |
I've solved. Was a Drive-QCliq motor so I don't need parameter p1982 = 1 so I set on 0. Now it works. |