Industry Online Support
Technical Forum
12/3/2011 4:49 PM | |
Joined: 6/4/2008 Last visit: 9/15/2024 Posts: 1497 Rating: (324)
|
Hi Mat, You don't state which technology type board you are using in the T300 family. I have assumed that because you are using CUMC drives, that you are using either the Angular Sync functionality (MS340) or the Positioning (MS380), so I attach the only manual I have for these. I will reply with the second manual due to the size restrictions. Searching for F116, seems to indicate a problem with MS340 = Overspeed MS380 = CBP Comms boards If you are not using CBP option cards, then this Fault needs to be masked out. Regards, Graeme
AttachmentMS380_e.pdf.pdf (228 Downloads) |
12/3/2011 4:50 PM | |
Joined: 6/4/2008 Last visit: 9/15/2024 Posts: 1497 Rating: (324)
|
Angular Sync Manual
AttachmentMANUAL.PDF (215 Downloads) |