5/9/2012 10:28 PM | |
Posts: 559 Rating: (87) |
Thanks a lot Nicky123, For your valuable reply. This will help to others also. |
5/10/2012 8:12 AM | |
Joined: 8/27/2006 Last visit: 9/2/2024 Posts: 719 Rating: (88) |
I have a question here, please. Nicky123said that he uses 4 load cells each of 20Kg. That makes his span of 80Kg. This span is equal to about 3000 digits for siwarex. Knowing that siwarex can transmit from 0 to 65536 digits, isn't it logic that from 0 to 80 equals (or nearly equals) 0 to 65536 digits ????? What is the difference if we have load cells of span 800Kg??? will this affect the accuracy???
|
Last edited by: AMAZINGAHMED at: 5/10/2012 8:13 AMThe more you know, The more you know that you don't know |
|
5/10/2012 2:20 PM | |
Joined: 8/27/2006 Last visit: 9/2/2024 Posts: 719 Rating: (88) |
Thanks for your reply, I got what you said, but in this case,Nicky123has calibrated using 80Kg as adjustment weight (which is full load) and the digits difference between 0 and full load was less than 3000 !!!! how is that possible??? or do I miss something??
|
The more you know, The more you know that you don't know |
|
5/10/2012 3:42 PM | |
Posts: 559 Rating: (87) |
My dear Friend AMAZINGAHMED, I think you got confused about what Nicky123 has written. Please read it carefully what it said is "Right now we are using 4 no,s of 20 Kg Loads for calibration." Means they are using 4 loads of 20 kg means total 80 Kg for calibration purpose only. Means for setting Adj weight 1 they are using 80 Kg load with 4 no.s of 20 Kg load. Am i right Nicky? Please correct me if I am wrong. Max load for the laodcell wold be different. |
This contribution was helpful to1 thankful Users |
5/14/2012 8:27 AM | |
Joined: 8/27/2006 Last visit: 9/2/2024 Posts: 719 Rating: (88) |
You are right, the adjustment weight is 80Kg, but the load cells capacity was not mentioned. Maybe I was just confused. So we need to know what is the capacity of load cells to decide weather there is a problem.
|
The more you know, The more you know that you don't know |
|
This contribution was helpful to1 thankful Users |
5/17/2012 4:51 AM | |
Joined: 6/13/2006 Last visit: 9/21/2023 Posts: 201 Rating: (8)
|
Hi, Your question is very general, at least you need to tell people which siwarex module for your application ? the dk800 is not Siemens product, therefore cannot compare the accuracy with siwarex weighing systems Regards, chook |
[IMG]http://i17.tinypic.com/66b7jas.jpg[/IMG] |
|
7/22/2013 2:29 PM | |
Joined: 9/1/2005 Last visit: 9/18/2024 Posts: 4104 Rating: (195) |
Follow up question split to seperate thread: weight system - I can not calibrate this! Best regards CS Moderator |