6/8/2013 1:00 AM | |
Posts: 49 Rating: (0) |
PCS7 V7.0
& Step7 V5.4+Sp3 |
6/10/2013 9:02 PM | |
Joined: 1/15/2009 Last visit: 4/19/2024 Posts: 316 Rating: (40)
|
ahmed, In order to upgrade the library you would need to upgrade the entire PCS 7 system (if your are interested, here are the linkshttp://support.automation.siemens.com/WW/view/en/39980937) But per CabreyTJ's screen capture you can swap out equivalent blocks with your current library and work just fine. Your Version - CabreyTJ Version (which is anything greater than V7.1 SP1) V7.0 - APL OP_A - OpAnL DEADT_P - DeadTime OP_D - OpDi01 Sel_R - SelA02In The other APL blocks for add, subtract, divide should be obvious. The F_TRIG and I_R are the same that you have in your current version. Good luck |
The best location for all PCS 7 content (manuals, guides, application notes, FAQs, and videos). |
|
6/23/2013 10:20 PM | |
Posts: 49 Rating: (0) |
hiii PCS7 V7.0 SP1
& Step7 V5.4+Sp3 best regards |
6/23/2013 10:59 PM | |
Posts: 49 Rating: (0) |
Hiii Bob i try to cahnge the value of cyclic memory but there is a limit of the range as in attachment how i can change the value? best regard
|
6/24/2013 10:53 AM | |
Posts: 836 Rating: (100)
|
Hi, this isn't such a good idea to change it to 9999ms.... Why do you want do do that? |