5/5/2012 2:21 PM | |
Joined: 7/2/2008 Last visit: 9/25/2024 Posts: 928 Rating: (308)
|
HelloRAJKIRAN,
You need this part number6ES7195-7HD10-0XA0for IM/IM bus unit. I recommend this part number6ES7153-2AR03-0XA0since it includes 2 IMs plus their active bus unit I hope you won't forget active bus units for I/O modules6ES7195-7HB00-0XA0. Also you will need deep S7-300 rail to mount the active bus units The CP5611 will work but in this case you will use the MPI for both redundant link and HMI communication. Don't forget it's only 187.5 kb/s. I recommend to use the CP443-1 lean bor both redundant link and HMI connection. In this case you will have 2 Ethernet lines one for each CPU and you may call it communication redundancy. In all cases you don't need the CP1623. Just use the integrated Ethernet port of the workstation. Don't forget to buy the software package6ES7862-0AC01-0YA0in order to have the blocks on STEP7 and WinCC faceplate and script. Best regards. H-H
|
Last edited by: H-H at: 5/5/2012 2:32 PMJust added the software package order number |
|
This contribution was helpful to2 thankful Users |
5/5/2012 5:27 PM | |
Posts: 947 Rating: (45) |
hello, RAJKIRAN I believe that you're trying too hard to solve the problem - as the problem of hardware redundancy. look at the manual http://support.automation.siemens.com/WW/view/en/1137637 |
Last edited by: gre_m at: 5/5/2012 5:47 PM |
|
5/10/2012 9:31 AM | |
Joined: 7/2/2008 Last visit: 9/25/2024 Posts: 928 Rating: (308)
|
HelloRAJKIRAN, Yes you can use the CP343-1 lean for both redundant link and WinCC. Best regards, H-H
|