2/5/2011 8:36 AM | |
Posts: 2964 Rating: (482)
|
Hi... You can short 56 and 14 and see movement is getting stopped....check the setpoint is voltage is cablepropely ..... You can controll the drift though the parameter P093..... and check? Have look on this document https://www.automation.siemens.com/doconweb/content.asp?item=12884&cd=sinumerik_simodrive_04_2010_e&scope=all Alarm list is attached for the reference.... Regards, Ekalavya Attachment611A_SP FAULT DETAILS.pdf (437 Downloads) |
2/17/2011 5:46 AM | |
Posts: 2964 Rating: (482)
|
Hello... Could you check the version information on the card? try using p51 / p151=10 and check? Hope fully it should happen.... Regards, Ekalavya |
2/17/2011 6:07 PM | |
Posts: 2964 Rating: (482)
|
Hello... Does it exactly matches your old card with the version(C/D/E)details? Regards, Ekalavya |
2/19/2011 3:22 PM | |
Joined: 6/7/2010 Last visit: 7/9/2024 Posts: 571 Rating: (37) |
Hello,Old controller card version is same: Version D. |
Regards, |
|
2/19/2011 5:01 PM | |
Posts: 2964 Rating: (482)
|
Hello... It should work.....Have you properly commissiong the card could try cross checking the same. For you reference i am attachinng the link... https://www.automation.siemens.com/doconweb/content.asp?item=12884&cd=sinumerik_simodrive_04_2010_e&scope=all Good luck.... Regards, Ekalavya |
2/23/2011 5:51 PM | |
Joined: 6/7/2010 Last visit: 7/9/2024 Posts: 571 Rating: (37) |
Hi, Card has been re commissioned, now the speed is matching. But some rubbing noise is in the motor, without rotating the motor.Could any one judge what may be the problem? |
Regards, |
|
2/23/2011 6:24 PM | |
Posts: 2964 Rating: (482)
|
Hi.... Does it is a bearing noise or the humming noise? try to check the parameters p31 and p32 reduce / incerease and check..... Regards, Ekalavya |