4/11/2012 3:06 AM | |
Posts: 303 Rating: (3) |
In my words status means whether the plc is in runmode,stop mode or fault mode.q |
4/11/2012 2:42 PM | |
Joined: 10/7/2005 Last visit: 9/23/2024 Posts: 3022 Rating: (1054)
|
HelloSaradhi have a look at SFB22 "STATUS", it'll allow you to monitor the Status of other CPU's (note that you'll need to configure a connection between the CPU's). I hope this helps |
Cheers |
|
This contribution was helpful to1 thankful Users |
4/14/2012 12:17 PM | |
Posts: 303 Rating: (3) |
But i need the status of the current cpu also. |
4/14/2012 4:17 PM | |
Joined: 3/21/2006 Last visit: 9/10/2024 Posts: 10228 Rating: (1181) |
For the current you can use SFC51. Reading PLC status with SFC51 The 'problem' is to read STOP state of CPU. Extracrt PLC Status (Run, Stop Indication) Best regards, Hristo Mihalev
|