Hello mhkocak,Some parameters can be changed during run, look in chapter 9.4 of the manual. If you canread out the actual speed in TP10 or set the max. speed limit in TP 8. Please note: For some Parameters (datatype DINT ENUM) you will need need the table in 9.4.12 In the application "flying sheres" the parameters for thesynchronisation are parameteredduring run (e.g. in Mode 4 (NW18) the synchronisation length is set in "Step 2" With a quick view, I did not found a parameter for this. Do you plan toexchange the encoder during run? |
|
|
8/13/2009 5:50 PM | |
Joined: 8/31/2005 Last visit: 8/20/2024 Posts: 2198 Rating: (328)
|
ok, I see. Changing the pulse rate is not possible, but changing the gear rate is. |
|
|