2/27/2015 7:46 AM | |
Posts: 1299 Rating: (136)
|
Hello, you can't insert a datatype as a tag. but if you have a tag in the plc with this data type (e.g. in a db) you can use this tag as an hmi tag. K!ke |
2/27/2015 8:36 PM | |
Joined: 9/21/2006 Last visit: 5/25/2023 Posts: 247 Rating: (65) |
I have been looking at this feature this morning. As best as I can figure out, in WinCC Adv V13 SP1 Upd1, you can create an HMI tag of a PLC user data type tag that is access symbolically. I can create the tag, and access the tag using absolute addressing, but I haven't figured out a way to access the tag symbolically, even though the tag itself is in an optimized data block in the PLC. Screenshots attached. I am hoping that I just haven't quite figured out how to do it yet. AttachmentUDT_HMI_Tags.zip (961 Downloads) |
3/11/2015 7:09 AM | |
Posts: 1299 Rating: (136)
|
Hello, it's possible with v13 SP1. https://support.industry.siemens.com/cs/ww/en/view/106567433 K!k1 |
This contribution was helpful to1 thankful Users |
6/10/2015 11:00 AM | |
Joined: 9/3/2014 Last visit: 3/13/2019 Posts: 4767 Rating: (123) |
|
7/6/2015 11:42 AM | |
Joined: 9/3/2014 Last visit: 3/13/2019 Posts: 4767 Rating: (123) |
|
8/7/2015 11:52 AM | |
Joined: 9/3/2014 Last visit: 3/13/2019 Posts: 4767 Rating: (123) |
|