4/9/2018 6:34 PM | |
Joined: 9/23/2005 Last visit: 3/14/2025 Posts: 4406 Rating:
|
Hi, The ET 200SP module DI 8x24VDC HS (6ES7 131-6BF00-0DA0) could be used also to high speed counting. In this way it could works with signal up to 10 kHz. All configurations are done in the device properties and the values/commands could be given directly by its IO interface. The “Libraries with PLC data types (LPD) for STEP 7 (TIA Portal) and S7-1200 / S7-1500” (https://support.industry.siemens.com/cs/br/en/view/109482396) make the use of the IO interface in the customer program easier. TIPs: 1 For easy use of the count value on program with comparators, you can change the data type of the read value from DWORD to UDINT or DINT. 2 Pay attention to not let "gaps" on the IO addressing when configure the Tag Table The follow cast (avi into a 7z into a zip) shows how to configure it. AttachmentHSC ET200SP DI HS.zip (1154 Downloads) |
Last edited by: Denilson Pegaia at: 6/6/2018 6:34:16 PMDenilson Pegaia |
|
This contribution was helpful to
8 thankful Users |
12/4/2019 7:06 PM | |
Posts: 1 Rating:
|
Hi Denilson, your video (from archive) is broken (have some broken position). |
10/15/2020 3:38 AM | |
Posts: 6 Rating:
|
Denilson, Thank you very much for the video and explanation! It perfectly worked for me! The video looks like it's "broken" because it stops for couple of minutes and then continue again. |
12/11/2020 12:16 PM | |
Joined: 9/24/2010 Last visit: 3/13/2025 Posts: 118 Rating:
|
Thanks Denilson Pegaia! It work with me. And i want to share my project to everyone.
AttachmentCoutingHSDI_20201211_1801.zip (846 Downloads) |
Mechatronic Center |
|
This contribution was helpful to
2 thankful Users |
Follow us on