10/17/2008 8:22 PM | |
Posts: 2661 Rating: (279) |
Hi Nil96, You do not need to "unlock" the block for doing this. Double click on the block (in blocks folder) and you'll see a pop-up that tells you that the block is protected. Click on OK to continue opening the block. The block is open in LAD/FBD/STL editor and you can see only the parameters (IN, IN_OUT, OUT etc.). Double click on the desired parameter and the Attributes tab select S7_m_c attribute and select value true. Save the block. In CFC you need to reimport the block (Options/Block Types/New Version) and recompile CFC. Also check the following FAQ's: How do you configure PLC blocks to enable their connections to be used in the OS system (WinCC)? Adapting blocks and libraries to the customer profile Regards |
10/18/2008 1:56 PM | |
Posts: 325 Rating: (13) |
Hi Phantom, |