Joined: 3/12/2015 Last visit: 7/17/2024 Posts: 533 Rating: (15) |
im going to go to the machine in about half an hour i will give you all the information then, |
9/5/2019 12:11 PM | |
Joined: 3/12/2015 Last visit: 7/17/2024 Posts: 533 Rating: (15) |
I'm not quite sure how to look that up but here is a photo of the adaptor... |
9/5/2019 12:31 PM | |
Joined: 4/23/2010 Last visit: 12/31/2023 Posts: 8092 Rating: (877)
|
Hello, 6ES7972-0CB20-0XA0 is not compatible with Windows 10. You need 6GK1571-1AA00. But with existing configuration I suggest you to use LAN cable & with LAN port on PC & X127 port on NCU you can go on line with PLC ladder. |
9/5/2019 1:08 PM | |
Joined: 3/12/2015 Last visit: 7/17/2024 Posts: 533 Rating: (15) |
I tried to do it wit a lan cable like you said but something else came up and it wont let me even find the device |
9/5/2019 1:54 PM | |
Joined: 3/12/2015 Last visit: 7/17/2024 Posts: 533 Rating: (15) |
My library... |
9/6/2019 6:37 AM | |
Joined: 4/23/2010 Last visit: 12/31/2023 Posts: 8092 Rating: (877)
|
Hello, How long this machine was down i.e. power was switched OFF? What alarm/error/fault is displayed? Please attach snap shot. Do you have NC PLC data back up? Which drives are installed? Sinumeric or Sinamics? Attached Library screen shot where from taken? Not clear. You need to set TCP/IP network properties & set IP address. For X127 port IP address is 192.168.215.1 NCU MLFB number is provided on sticker which is at right side cover of NCU. Please refer attached snap shot. From NCU MLFB PLC CPU details can be confirmed. 6fc5203-0af00-0aa1 is OP & not HMI software. HTH |
7/9/2021 9:03 PM | |
Joined: 2/27/2021 Last visit: 4/24/2024 Posts: 1 Rating: (0) |
Hi did you got this solved? Im having the same error |
8/8/2021 7:09 PM | |
Joined: 7/29/2021 Last visit: 1/26/2024 Posts: 1 Rating: (0) |
Conseguiu comunicar com sinumerik 840d? |