11/4/2010 3:36 PM | |
Joined: 7/28/2010 Last visit: 8/31/2024 Posts: 184 Rating: (11) |
Melwyn, By other drives, you mean the control unit of other drives? If you lose 380VC tothe Drive modules, the module will tripbut control unit can stay up and running if you have a UPS which protects the 24VDC. Regards, Behnam www.sigmaprocess.ca |
11/4/2010 5:06 PM | |
Joined: 6/4/2008 Last visit: 9/15/2024 Posts: 1497 Rating: (324) |
Hi, if you have a load with some kinetic abilities (i.e. inertia) then you can activate the VDC kinetic buffering which in the event of a power dip utilises the kinetic energy of the load to generate some power to keep the DC link within its tolerance band. If you are driving a small pump or similar, then this probably won't be useful. Download the manual (Operating Instructions) for the G150 fromhere, you will have to select the relevant firmware version of your manual. See the section labelled "Drive functions - VDC Control" Regards, Graeme
|