Joined: 8/31/2005 Last visit: 8/20/2024 Posts: 2198 Rating: (328) |
see manual https://support.industry.siemens.com/cs/ww/en/view/109763271 STW is on page 2081 and following ZSW is on page 2100 and following |
Last edited by: miami at: 09/21/2020 13:23:22 |
|
9/21/2020 2:03 PM | |
Joined: 1/17/2013 Last visit: 9/20/2024 Posts: 1104 Rating: (6) |
Dear miami, Thank you for you manual. But if you more explain about each value meaning status of drive it is better is possible. Best Regards, Vorapob |
Best Regards, |
|
9/21/2020 2:49 PM | |
Joined: 7/7/2010 Last visit: 9/23/2024 Posts: 15217 Rating: (2417) |
You cannot mean you do not understand any of the status or control word bits, or do you? Please post the exact control and status word bits that you do not understand the meaning of. For example, if you do not understand any of the reserved bits, we on this forum cannot help you.
|
science guy |
|
This contribution was helpful to1 thankful Users |
9/22/2020 10:50 AM | |
Joined: 8/31/2005 Last visit: 8/20/2024 Posts: 2198 Rating: (328) |
RFG = ramp function generator (page 2209 and 2210 in the manual) |
|
|