Please also see attached screenshots. I need to change the PW for a user on a WinCC 7.4 server we have. I open the project (integrated project in Simatic Manager) and I open the WinCC project and change the PW for the user. In Simatic manager I select the WinCC project and rightclick and select download. I get the indication that it will do a partial DL which is nice. But then it claims that the RT is not obtainable and in the error log I am told to "Please check the terminal bus configuration" So - what is the "terminal bus configuration" and how do I make it work? I CAN go compare and go online on PLC blocks so the connection is working. AttachmentOLM DL.zip (56 Downloads) |
11/27/2019 2:38 PM | |
Joined: 2/18/2013 Last visit: 7/11/2024 Posts: 139 Rating: (12) |
Terminal busThe terminal bus must be configured for the right network card in the SIMATIC shell. If you are using multiple network cards, there is the danger that the network card via which the WinCC communication is supposed to run is not selected here. Another indicator that the network is functioning (availability of the other computers) is that you can see the projects of the other computers in the network in the SIMATIC shell. |