I would like to refresh the topic due to the problem with using Configuration control with communication modules. I try to disable RS232 module in slot 101 and i can't. I get status 0070_0200 and PLC is sill in startup mode (I have a loop in OB100 to wait for the end of WRREC execution and it never done). I made some testes and if I remove the module from hardware permanently - all works well and PLC goes to run. If I have this module in hardware then is no matter what I set in the slots 101 - 103 in the data records - PLC never go to the RUN mode. The same PLC has also program disabled IO modules and these works flawlessly. I have checked all siemens tutorials and I don't see any faults in my config - I tried all methods and no effects. If anybody has some idea for this? I use TIA V15.1 Ok I have found the answer and topic is off. Modules changes is not possible to communications modules - these must be the same as configured in hardware. So in my case I have to make a second project without these modules. ------------------------------------------------------------------------------------------ |