Hello Rakib; A Bacnet OPC server would be the best way to connect WinCC v7.x to a comm partner that does not support the built-in drivers for WinCC. Once you have connected the OPC server to your Bacnet equipment, use the WinCC OPC channel to configure exchanges to the OPC server. Follow the instructions in the following document to configure WonCC as an OPC client; What steps are required to start up a WinCC station as OPC server or as OPC client (OLE for Process Control)? https://support.industry.siemens.com/cs/us/en/view/12069091 This document from Siemens suggests Top Server UCON drivers (by Software Toolbox, pages 10 and 11) to connect to WinCC v7 and WinCC TIA Portal. Note that there are many manyfacturers of OPC servers that can be used in this type of project, such as Matrikon, Kepware... Hope this helps, |
Last edited by: dchartier at: 07/13/2019 15:32:08 |
|
7/15/2019 10:27 PM | |
Joined: 9/28/2017 Last visit: 8/28/2024 Posts: 64 Rating: (0) |
Thanks for the reply. can you help me by sharing some details about the procedure? |