Hello biguri you will not "see" all availableports of your X208 switch in HWconfig, it isjust a Profinet I/O device as far as the S7 CPU (the Profinet I/O Controller)is concerned. To define the Topology, you'll need to right click on the X208 switchand select "Profinet I/O Topology" from the drop down menu. Having said that, definition of the Profinet Topology is optional, your Profinet I/O network should work whether you configurethe Topologyor not. Please note though that the X208 is a managed switch (not an unmanaged one nor a hub) and requires some configuration to start with (see its manual belwo for more). Here are some hopefully useful linksto get you started with your task and please revert back here for more questions if they don't: PROFINET IO - Configuration & Diagnostics Industrial Ethernet Switches SCALANCE X-200 / XF-200 Operating Instructions Network topology with SCALANCE I hope this helps |
Last edited by: fritz at: 7/6/2010 1:38 AMCheers |
|
This contribution was helpful to1 thankful Users |
7/10/2010 10:36 AM | |
Posts: 14 Rating: (0) |
Thanks a lot for you help, I'll try it and if I have any problem I'll let you know. Really thanks |
7/14/2010 12:08 PM | |
Joined: 4/6/2006 Last visit: 2/5/2024 Posts: 604 Rating: (56) |
Hi, About Layers i would say try google and wikipedia: OSI-Model About the Scalance W. You first have to assign a IP-Adress to the device with for example the Primary Setup Tool, download is available on this website. Just use the search box. As you have assigned an IP-Adress to the devices you can enter the Web Based Management to set all the parameters. See Chapter 3.2 of the manual in the link below. I just wonder or you've had a look in the product manuals for the Scalance W products you use. There is some information about the different MC-modes available. See Chapter 3.1.8 in the manual linked below. SCALANCE W-700 Configuration Manual |
Best regards, |
|