Hello, you can't use the NPN-signals directly at your CPU or the FM350. If you need the signals for counting then can you convert the signal from NPN to PNP with a converter e.g. Switching amplifier - DEK-TR/INV - 2964319 from Phoenix Contact. If you need "only" slower inputs then can you use the Digital input module SM 321; DI 64 x DC 24 V, sinking/sourcing; (6ES7321-1BP00-0AA0) regards |