11/1/2020 4:53 PM | |
Joined: 3/28/2015 Last visit: 11/7/2024 Posts: 721 Rating: (213) |
Hello,
|
Eng.Mohamed Ibrahim |
|
This contribution was helpful to1 thankful Users |
11/2/2020 2:40 PM |
|
Joined: 7/7/2010 Last visit: 11/15/2024 Posts: 15402 Rating: (2446) |
.. |
Last edited by: 0_Einstein at: 11/02/2020 22:57:51correction - my prior post was *wrong* science guy |
|
11/2/2020 6:13 PM | |
Joined: 3/28/2015 Last visit: 11/7/2024 Posts: 721 Rating: (213) |
Hello, Please have a look at the attached photo. The 4-wires transmitter is an active 4-20mA output. The 2- wires analog input module is an active module. You can't install 2 active components directly in the loop. You need to install the Isolator with passive(sink) output between 4-wires transmitter and 2- wires analog input module. |
Eng.Mohamed Ibrahim |
|
11/28/2022 1:18 PM | |
Joined: 6/19/2017 Last visit: 9/6/2024 Posts: 8175 Rating: (172) |
New question published by Booleans is split to a separate thread with the subject Which type of Isolator can be used ?. Best regards |
Follow us on