4/14/2018 9:17 AM | |
Joined: 4/23/2010 Last visit: 12/31/2023 Posts: 8092 Rating: (877) |
Hello, To test 1FK7063-5AH71-1GB3 motor on 611U drive you need 6SN1118-0NH01-0AA1 or 6SN1118-1NH01-0AA1 control module. 6SN1118-0NH00-0AA0 card is not capable to interface the above said motor encoder. Also you need 6FX5002-2CH00-XXXX type signal cable to interface motor absolute encoder to control card. 6SN1123-1AA00-0CA1 power module is OK to power the motor. User may connect analog input to terminal 56.x/14.x or terminal 24.x/20.x. Please refer the SIMODRIVE 611 universal SIMODRIVE 611 universal E, Control Components for Closed–Loop Speed Control and Positioning manual for hardware connection & software which will help you to test your motor with drive. For commissioning of drive, Simucom U software is available which you may download from SIMODRIVE 611U package V14.03.01 link. HTH. |
Last edited by: PISCEAN 2010 at: 4/14/2018 9:30:00 AMSimucom U web link added Last edited by: Jen_Moderator at: 4/16/2018 10:10:29 AMOptimized links. |
|
4/15/2018 12:12 PM | |
Joined: 6/21/2014 Last visit: 9/11/2024 Posts: 41 Rating: (0) |
HELLO YES .I REPAIR THE MOTOR BY REPLACING BALLBEARING BUT I DON'T READ THE PDF YOU MENTIONED COMPELETLY. YET . BECAUSE IT IS TIME CONSUMING.THE MODULES USED IS : 6SN1123-1AA00-0CA1 POWER UNIT AND 6SN1118-0NH01-0AA1 CPU CARD. AND INFEED MODULE. 6SN1145-1A00-0AA1 AND THE MOTOR IS NO LOAD.THE BRAKE IS EXTERNALLY EXITED. I WANT TEST THE MOTOR IN MY WORKSHOP .I BUILD MOTOR CABLE FOR POWER AND ENCODER.THE ENCODER CABLE I BUILD IS SEEN IN ATTACHMENT. THANKS AttachmentABSOLUT ENCODER CABLE.pdf (529 Downloads) |
Follow us on