Dear Expert, If I m going to select 3WL ACB with 4000A & I want spring charge indication, then pls suggest for wiring scheme & terminal connection of ACB.
|
7/1/2013 9:19 PM | |
Joined: 7/8/2009 Last visit: 7/26/2023 Posts: 1974 Rating:
|
Look at Configuration Manual SENTRON 3WL Air Circuit Breaker On Page 49, you will find connection diagram Connect accordingly Hope this will help you Regards, Devesh Vithani |
I dont Like people driving Fast, thats the reason I overtake them ;) |
|
7/2/2013 6:53 AM | |
Posts: 1064 Rating:
|
check pg 49 of the manual connector x7 terminals 10 and 11 |
This contribution was helpful to
1 thankful Users |
7/2/2013 6:59 AM | |
Posts: 1064 Rating:
|
sorry i didn't see you mention page number |
This contribution was helpful to
1 thankful Users |
7/10/2013 1:24 PM | |
Posts: 235 Rating:
|
Attachmentspring charge indication.pdf (467 Downloads) |
7/10/2013 1:42 PM | |
Joined: 11/21/2007 Last visit: 6/24/2024 Posts: 2324 Rating:
|
Hello S20 ( As the name says ) is a "Ready to Close" Contact and cannot be used for "Spring Charged" You need to use S21 ( Available on Trip X7 Terminal No 10-11 ) - Pl see Attached Wiring. As already mentioned this terminal is not available if COM 15 / COM-16 is installed Hope this helps Cheers Navnag AttachmentSENTRON_Wiring.pdf (435 Downloads) |