7/12/2024 12:33 AM | |
Joined: 11/19/2023 Last visit: 7/14/2024 Posts: 1 Rating:
|
Hi every body, I have to create interlock when temp of cement reached 115 should I force the water injection system to be increase his manual setpoint by 300 liters i took the manual set point and used the add instruction to add the 300 l in the tia portal V16 but the problem is that the plc will add the amount and consider the last result as manul set point and add the 300 l again and keep doing this until reach the max set point could you help how to add the 300 only one time thank you ------------------------------------------------------------------------------------------ |
Last edited by: Wit_Moderator at: 07/12/2024 13:01:16New subject after splitting |
|
7/14/2024 6:44 AM | |
Joined: 1/27/2009 Last visit: 8/15/2024 Posts: 171 Rating:
|
Hello Huss1122, As jacek d suggested
And he is absolutely right. But let's dig a little bit into your problem. Your tag "manual setpoint" is a configuration tag of some control system. Configuration tags must not be changed programmatically, they should be constants or changeable by the process operator only. |
The only thing necessary for the triumph of evil is for good men to do nothing |
|