5/31/2010 6:35 AM | |
Joined: 3/21/2006 Last visit: 11/1/2024 Posts: 10229 Rating: (1181) |
Hello, I'll try to answer of your questions.In the beginning we should say that configure your LOGO! to use either two or four analog inputs as described in topic "Setting the number of AIs in the Basic Module" part of Manuals, configurable:LOGO! . When using inputs I1, I2, I7 and I8 as analog inputs, only the range from 0 to 10 V DC is available. 1. Yes, you can "simulate" directly AI. Just be careful for inputs current and voltage limits. 2. No, I think you couldn't make limit of 5V. Eventually in software to make some "interpretation"... Best regards, Hristo Mihalev |
Last edited by: UMENCHO at: 5/31/2010 7:39 AM |
|
5/31/2010 7:30 AM | |
Posts: 32 Rating: (0) |
Hi, First of all, I would like to thank you for your reply. But your analog inputs as described in topic "Setting the number of AIs in the Basic Module" cannot be view. Where else can I view this module (website)? I looking forward your reply. Thanks nelson |
5/31/2010 7:39 AM | |
Joined: 3/21/2006 Last visit: 11/1/2024 Posts: 10229 Rating: (1181) |
Hello Nelson, Sorry! This is part from Manuals, configurable:LOGO! |
This contribution was helpful to1 thankful Users |
Follow us on