Hi, In that case, I would recommend you try to change port 5900 to another one which is not in use (5909, for example), both in the parameterization of the SmartServer in the HMI panel and consequently after when accessing it from the SmartClient. Basic Panels manual - Configure Sm@rt Server It would also be interesting to install the latest released image version for your Basic Panel: Image Downloads for SIMATIC HMI Operator Panels: Comfort / Mobile / Basic Panels |
A rating will be well appreciated. |
|
This contribution was helpful to1 thankful Users |
10/2/2024 12:44 PM | |
Posts: 3 Rating: (0) |
I will do what you say. Are the HMI settings in the picture correct? |