10/13/2020 1:27 PM | |
Joined: 9/27/2006 Last visit: 9/11/2025 Posts: 12406 Rating:
Hello kprahul; Rockwell provides a migration guide from Logix 5000 to Siemens S7-300 CPUs, which detail the I/O modules of each family in Appendix A: - Simatic S7 to Logix5000 Application Conversion Guide https://literature.rockwellautomation.com/idc/groups/literature/documents/ap/logix-ap008_-en-p.pdf Siemens provides a descriptive guide to their digital I/O modules in this manual, Chapter 4. - SIMATIC S7-300 S7-300 Module data https://support.industry.siemens.com/cs/ww/en/view/8859629 Unfortunately, you seem to be working with an old SLC 1746 controller, which Rockwell treats as dated. There are still documents available for their I/O modules but no comparison to S7 CPUs.. - SLC I/O modules Based on the documents above, I have attempted to link the I/O modules used in your SLC project to a Standard S7-300 configuration. I leave it to you to confirm these part numbers, or select modules closer to your application.
The module you have in stock, 6ES7323-1BH00-0AA0 is a mixed 16 DI/16DO 24 VDC module, maybe you can use it for some of your controls, but it will not match certain requirements you have. https://support.industry.siemens.com/cs/pd/364671?pdti=td&dl=en&lc=en-WW Finally, this article discusses sourcng and sinlking modules in Siemens 24 VDC I/O modules, with details for certain I/O modules: - What is the meaning of the terms "sinking" (German: "P-lesend") and "sourcing" (German: "M-lesend") in digital modules of SIMATIC? https://support.industry.siemens.com/cs/ww/en/view/23451499 Good luck, Hope this helps, Daniel Chartier |