10/29/2014 9:04 AM | |
Joined: 4/22/2010 Last visit: 3/31/2025 Posts: 5697 Rating:
|
Hello, If the machine is still running, there must be a program in it. You can upload this program (without Symbols and Comments) You need Step5 software and a interface cable or a PG. Read more : SIMATIC STEP 5 V7.2Chapter 4.2.2 If you are not sure you can do the job, hire someone with a PG to do the job for you. Regards, Marcjan |
Last edited by: Marcjan at: 10/29/2014 9:15 AMProblem solved? |
|
This contribution was helpful to
1 thankful Users |
10/29/2014 9:07 AM | |
Joined: 11/21/2007 Last visit: 7/25/2025 Posts: 2326 Rating:
|
Hello It is difficult to make out from the picture. I can seeseveral DIsGlowing but no DOs ( This may be due to program logic or maybe the PLC program is lost . The S5 95U executes the program from the internal RAM with EPROM / EEPROM as backup storage. The RAM program is lost if the PLC is powered off with the battery removed or battery voltage LO. if the PLC is in operation ( It is executing the program and doing the control operation as required ) then it is possible to upload the program from the CPU. You can contact your local siemens contact / service provider for the same. Good Luck !! Cheers Navnag Marcjanhad already posted the reply while, I was probably editing mine. ...
|
Last edited by: Navnag at: 10/29/2014 10:15 AMFootnote added There is no such thing as the last bug in a program |
|