2/16/2024 8:02 AM | |
Posts: 1 Rating:
Hi, Can we use this digital output module at 5000m site? 6ES7222-1XF32-0XB0 I found document that says most of S7-1200 product can be used. This one is not mentioned in it. [snip] Attachments71200_s71200f_product_information_x_en-US_en-US.pdf (481 Downloads) |
2/16/2024 12:38 PM | |
Joined: 7/27/2023 Last visit: 8/28/2025 Posts: 131 Rating:
Hi! In the attached document, from 2019, the module does not appear. The release of the module was in 2013 https://support.industry.siemens.com/cs/us/en/view/80461891 so if it is not included in the PDF it is likely not allowed. In any case, I recommend you contact a Siemens sales representative. |
2/19/2024 11:23 AM | |
Joined: 10/25/2022 Last visit: 9/9/2025 Posts: 21 Rating:
On page 142 (3/72) of Catalog ST 70 - 2023 The different versions of 6ES7222-1XF32-0XB0 are listed, and they all have a maximum altitude of 2000m above sea level |
This contribution was helpful to
1 thankful Users |
2/19/2024 1:55 PM | |
Joined: 7/7/2010 Last visit: 9/9/2025 Posts: 16077 Rating:
Oh, you meant 5000m above sea level is the physical site where the dig out module would be installed?? I interpreted the question as help sending the dig out signal 5000m away from the module's terminals.
science guy |
Follow us on