salut, tu as fait le changement dans le panneau de configuration du pc ou dans "online access" de l'IHM ? MERCI |
5/23/2024 1:38 PM | |
Joined: 8/21/2014 Last visit: 9/3/2025 Posts: 1091 Rating:
|
Hello joval972, Please try to discuss your question in English language. This is an internationalcommunityand we try to focus on one language. Posting in English will help you to get more response to your question. This is the translation of your question:
Best Regards, The Helping Hand |
My Forum is the place to personalize your profile, |
|
12/18/2024 2:03 PM | |
Joined: 4/24/2006 Last visit: 7/31/2025 Posts: 9027 Rating:
|
Hello, Do you have software TIA Portal v15, then you can download to panel. (You will get a message to update the Operating System. ) Have a look at: How do you do a SIMATIC HMI operating system update (firmware update, OS update) on operator panels or perform a "Reset to factory settings"? When you not want to upgrade your panel, then you will have to use TIA Portal v13 to download project to panel. Best regards, Wizard |
3/6/2025 12:39 PM | |
Joined: 2/17/2025 Last visit: 5/22/2025 Posts: 1 Rating:
|
Am having the same problem can someone help please |
7/22/2025 3:59 PM | |
Joined: 4/24/2025 Last visit: 7/22/2025 Posts: 1 Rating:
|
Hey I found solution. In SET PG/PC INTERFACE in Acces Point of the Application u should set CP_L2_1 -> Ur network Card |