9/12/2010 2:39 PM | |
Joined: 6/4/2008 Last visit: 8/5/2025 Posts: 1518 Rating:
|
Hi, really simple. See the attached function diagram 190. P590 drives Control word 2 bit 30. When you doubleclick on a relevant parameter in Drivemonitor, it gives you the option to enter a Binnector value. For example, if you entered B14 (Digin3) into P590, then digital input 3 would be used to flick between the two BICO sets you mentioned. i.e. using your quoted example, if Digital input 3 is 0, then P554.1=10 would be used, which means that digital input 1would be used to turn the drive On/Off, however, if Digin3 = 1, P554.2=2100 would be used so source of the On/Off would be via the Serial communications word Bit 0. Hope this clears up any confusion. Cheers, Graeme AttachmentBasic Function Diagram 190.pdf (386 Downloads) |
This contribution was helpful to
1 thankful Users |
Follow us on