7/2/2020 2:29 PM | |
Joined: 9/6/2015 Last visit: 4/17/2025 Posts: 141 Rating:
|
Hi That's an interesting problem. Can you export your HW then upload it? |
9/16/2020 1:18 PM | |
Joined: 9/9/2015 Last visit: 4/9/2025 Posts: 732 Rating:
|
Dear tgrevenstuk1979, If you use 2 wire configuration, ensure you have added a jumper between 10 and 11 at the AI Module front connector. |
Please give me 5 stars Rating if my post is helpful for you. :) |
|
12/4/2022 8:16 AM | |
Joined: 9/9/2015 Last visit: 4/9/2025 Posts: 732 Rating:
|
Just to add on top of this topic. PCS 7 V9.0 SP3 UC04 Step 7 V5.6 + SP2 + HF9 FAI Module - 6ES7 336-4GE00-0AB0 DP Slave Diagnostics - Slot xx - Channel 00 - ambiguous error. Channel organized bit by bit SAFE LED - off (Dip switch correctly set) Unable to work properly. My workaround solution: 1. Remove the front connector 2. Remove the slot from bus unit 3. wait 10seconds 4. insert the slot on the bus unit 5. insert the front connector back to the slot. 6. wait for 10 seconds 7. SAFE LED on. 8. Module work properly.
|
Last edited by: JazTai at: 12/04/2022 08:17:24Please give me 5 stars Rating if my post is helpful for you. :) |
|
This contribution was helpful to
2 thankful Users |
Follow us on