8/1/2022 4:16 PM | |
Posts: 71 Rating:
|
Hello KateT, In a SCADA system you have to separate the 3 buses in different subnets, and each one with its specific network card: redundancy (connection between redundant servers), terminals (WinCC server-clients connection) and plant (connection with PLCs, periphery, etc.). As you have it now, it would not be separated and this may be the reason causing this problem. To add some relevant information, I recommend you to check the following example: - Redundancy in WinCC V7.x and WinCC Professional https://support.industry.siemens.com/cs/ww/en/view/109772627 Best regards, S7-mencey. PD: If this post helped you, don't forget to rate with 5 stars! |
8/3/2022 12:10 PM | |
Posts: 71 Rating:
|
Hello KateT, In the following manual, you can check detailed information about communications with several network cards in WinCC 7.5. Specifically in page 63. - WinCC V7.5: Configuration and communication https://support.industry.siemens.com/cs/ww/en/view/109760748 Page 63: Specifics of Communication for a Server with Several Network Cards Best regards, s7-mencey. PD: If this post helped you, don't forget to rate with 5 stars! |